Charge start causes solar inverter RCD to trip

Featured Replies

DC leak injection testing at start of the charge causes SolarEdge inverter to produce a fault and needs time to start producing again.

I have automated charging of the car when there is excess solar production. How do I disable DC injection test that is done each time charging starts?

Wouldnt it make sense to test DC leak on each startup instead of each charge start?

Thanks.

Do you have a WARP1 Charger or WARP2/3 Charger?

WARP2/3 can not cause a RCD to trip. With WARP1 a type A RCD can be tripped if there is a dc leakage current, but not during any testing.

  • Author

Hi, apologies for not stating - I have WARP3 11kW Pro charger bought a month ago. See TLDR below.

Solar inverter (SolarEdge 16K) shows it faults due to RCD Over Current - I assumed due to DC injection for self-test because dedicated RCD 30mA AC for EVSE never tripped. See screenshots below of Home Assistant and SolarEdge status..

The fault occurs each time car is plugged in and charge starts. If charging is restarted without unplugging, the fault doesn't occur.

This didn't happen before with Aliexpress KHONS charger which also had RCD DC protection built in so I'm puzzled what else could be causing this.

I could borrow a scope and take measurements when 'fault' occurs.

I've tried toggling

  • "EV Wakeup" option on WARP3

  • Pressing "Test DC fault pro­tec­tor" button on WARP3 while charging - but it doesn't fault the charge session.

TLDR

I've now tried reseating Lighting surge protection devices (from the solar junction box) that can bridge phases and neutral with ground and I can no longer reproduce the RCD fault at either 6 or 16A current set on the WARP3.

Seems the issue is resolved.

Thank you anyways.

image.png

image.png

image.png

On 6/12/2026 at 4:52 PM, Radko said:

Pressing "Test DC fault pro­tec­tor" button on WARP3 while charging - but it doesn't fault the charge session.

The DC fault protector can only be tested when no car is plugged in. Which is also why the DC fault injection cannot cause any problems when a charge is starting.

The DC fault "Differential Current Sensor" that we use in the WARP3 is a fluxgate current sensor. For testing it has an auxiliary winding in the toroid where it can induce test currents.

It does not actually touch the live wires at all. It is physically impossible for the sensor to induce a fault current in your live wires that go into the solar inverter.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

Account

Navigation