hi, I have a simple setup next to the POOL that includes a POE powered Master brick with 4 bricklets.

1)PTC

2)Dual Relay (pool pump, pool lights)

3)Dual Relay (garden light, not used)

4)I/O 4port when I use 2 ports for manual switches for pool pump and pool lights

 

Now the trick is that when I connect my EV charger to the car (10A) that is on the same phase as pool pump. I/O ports will close for a short time as if the button would be pressed. This will start the pool pump and lights.

 

I'm guessing there is some interference from the Dual Relay going into the I/O 4port, but how is that possible? From an OH2 log I can see that i/o 4 putton press takes aboout 200ms, Any ideas how to mitigate such a problem?

 

2018-04-04 22:48:57.874 [itemStateChangedEvent     ] - Pool_in2 changed from OPEN to CLOSED
2018-04-04 22:48:57.881 [itemStateChangedEvent     ] - Pool_in3 changed from OPEN to CLOSED
2018-04-04 22:48:57.901 [itemCommandEvent          ] - Item 'Pool_Relay1_ligths' received command ON
2018-04-04 22:48:57.911 [itemStateChangedEvent     ] - Pool_Relay1_ligths changed from OFF to ON
2018-04-04 22:48:57.923 [itemCommandEvent          ] - Item 'Pool_Relay2_pump' received command ON
2018-04-04 22:48:57.925 [itemStateChangedEvent     ] - Pool_Relay2_pump changed from OFF to ON
2018-04-04 22:48:57.957 [DEBUG] [eclipse.smarthome.model.script.OTHER] - --------- Pool Pump Timer sleep time:7200000
2018-04-04 22:48:58.071 [itemStateChangedEvent     ] - Pool_in2 changed from CLOSED to OPEN
2018-04-04 22:48:58.076 [itemStateChangedEvent     ] - Pool_in3 changed from CLOSED to OPEN

 

Link zu diesem Kommentar
Share on other sites

How do you detect the button press? Do you use the internal pull-ups from the IO-4 and the button shorts to ground?

 

If that is the case, you might want to add an additional pull-up (perhaps 1k or similar). The internal processor pull-up is specified to be somewhere between 100k and 400k, which might be to little resistance for the interference from the pump?

Link zu diesem Kommentar
Share on other sites

  • 4 weeks later...

On I/O 4 I have a button that shorts The pin to board ground. Detection is done by Tinkerforge OpenHAB binding. I do not understand pull-up sugestion. You want me to add a 1Kohm resistor in the button circuit? The interference does happen if the button is  disconected and the I/O4 is simply conneted to the brick without any pin connected.

 

For now I have a rough workaround. Since the interference is shorting the pins for about 200ms. I wrote openhab rule that requires 2 sec button press to enable the pump or lights in Pool. But the problem is still there.

Link zu diesem Kommentar
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Gast
Reply to this topic...

×   Du hast formatierten Text eingefügt.   Formatierung jetzt entfernen

  Only 75 emoji are allowed.

×   Dein Link wurde automatisch eingebettet.   Einbetten rückgängig machen und als Link darstellen

×   Dein vorheriger Inhalt wurde wiederhergestellt.   Clear editor

×   Du kannst Bilder nicht direkt einfügen. Lade Bilder hoch oder lade sie von einer URL.

×
×
  • Neu erstellen...